I am hoping I can get some feedback from you guys concerning the correct wire sizing for a 112.5 KVA transformer. We are planning on feeding it from a 480/277 panel with a 150amp breaker. we are going to install a 200amp disconnect before the transformer and reduce the fuse size to 150 also. The length is 300' from the 480/277 panel to the disconnect. I am saying that we can use #1 THHN and a #2 GND, but my boss is saying we need to run #1/0 THHN. What about bonding bushings? At the panel, or when we enter the transformer from the disconnect? We are planing on installing a 300 amp 120/208 panel off the secondary side with # 350MCM. My boss doesn't do alot of commerical work, and on most jobs I worked on in the past that information is already laid out for you from the shop. Is there anything else that we are missing? I do believe I saw something about grounding the transformer to the building steel also. Just trying to help the guy out. Any thoughts???

Nothing We Do Is Worth Getting Hurt!

kbsparky
Moderator

USA
1976 Posts

Posted - 12/19/2009 :  00:33:28  Show Profile  Visit kbsparky's Homepage  Send kbsparky an AOL message  Send kbsparky an ICQ Message  Send kbsparky a Yahoo! Message  Reply with Quote
The capacity of #1 copper is 130 Amps. Your transformer operating at 100% load will draw 135 Amps.

Depending on what you have connected to it will determine whether you will ever approach this value.

Since the next standard size of breaker is 150 Amps, you are permitted to use that size breaker on the #1 conductor provided your total connected load does not exceed 130 Amps. The ECG only needs to be a #6 on the primary side of this transformer.

Bonding bushings are required where concentric or eccentric knockouts are encountered (over 250 Volts), or where flexible conduit is used. However, you may not need those if a separate EGC is installed with your circuit conductors in the flex.




-KB



Life is uncertain -- Eat dessert first !!
Go to Top of Page

Dyne2798
Member

USA
21 Posts

Posted - 12/19/2009 :  13:26:22  Show Profile  Visit Dyne2798's Homepage  Reply with Quote
Thanks for the post

Nothing We Do Is Worth Getting Hurt!
Go to Top of Page
  Previous Topic Topic Next Topic  
 New Topic  New Poll New Poll
 Reply to Topic
 Printer Friendly
Jump To:
               

Who's On:
7 People
Google Bot
 Electrical Forum
207.46.1..?
 Electrical Forum
91.212.2..?
 Archive - Electrical Distributors, Inc.
206.53.1..?
 DwellingCalc
65.55.25..?
 Electrical Forum
212.190...?
 Electrical Forum
95.211.8..?
 Electrical Forum
Electrical Knowledge Repository © 2000-2002 Electricalknowledge.com Go To Top Of Page
This page was generated in 0.12 seconds. Snitz Forums 2000