PHILLIP
New Member

USA
2 Posts

Posted - 04/07/2009 :  07:35:32  Show Profile  Visit PHILLIP's Homepage  Reply with Quote
Is it safe to backfeed a delta to wye. I have a 480 VAC wye input and I want a 440 VAC delta output. What type of issue (ground) can I expect if I move forward with this. An alternative I have in mind it to use a buck boost--> autotransform which I beleive will also work.

PHIL

Mshea
Avid Member

Canada
150 Posts

Posted - 04/08/2009 :  10:42:16  Show Profile  Visit Mshea's Homepage  Reply with Quote
Using an isolation transformer to buck the voltage for a piece of equipment is expensive as compared to a buck transformer. Usually the buck boost transformer only needs to be 10% of the current rating. Transformers work both directions so Wye to Delta does work.
I just realized you also asked about grounding, The secondary of an isolation trasformer (not the medical kind of isolation) will result in an ungrounded secondary and ground detection lights would also be required. Use a buck transformer so the ground works.
Go to Top of Page

PHILLIP
New Member

USA
2 Posts

Posted - 04/09/2009 :  15:19:30  Show Profile  Visit PHILLIP's Homepage  Reply with Quote
Forgive me, I am an electrical engineer with little experience in grounding issues. I will be using the backfeed, I have no say in that. I have had my circuit approved. What are ground detection lights?


PHIL
Go to Top of Page

DC1
Avid Member

USA
125 Posts

Posted - 04/10/2009 :  14:46:09  Show Profile  Visit DC1's Homepage  Reply with Quote
Phil, Why do you need a Delta output? If you need to drop the voltage, use your correction taps on the delta side and feed the transformer from the delta side. If you are trying to get a sitiuation where the first fault is free, in other words the first fault does not cause a machine or the whole plant to shut down, then perhaps you should look in to a high resistance grounding system, which will come with its own fault detection system.

http://www.postglover.com/highresistancegroundingvideo.html

Daniel Carter
Instrumentation and Control Technician
Perfromance Pipe
Go to Top of Page

Mshea
Avid Member

Canada
150 Posts

Posted - 04/14/2009 :  17:22:04  Show Profile  Visit Mshea's Homepage  Reply with Quote
Phillip since a delta connected transformer has no ground when a leg does get grounded no over current device will trip but the enclosure will have a live conductor connected to it. If a second phase should ground the resulting connection would be a phase to phase fault and the resulting damage would also be greater. As you know the stress on the insulation would be phase to phase instead of phase to ground. So 440 volts instead of 256. A ground detection light is a neon bulb connected from each phase to ground rated at the phase to phase voltage. When a ground fault occurs the bulb connected to the phase that is faulted goes out and the other 2 get a little brighter. This obviously lets you continue working but without the indicator no one starts looking for the fault.
Do a damage curve at 256 volts and one at 440 volts to see the incident energy available.
I had inserted a comment here regarding the posters experience and in retrospect I was out of line. Philip I appologise if my comments were taken in offence. This forum is for electrical professionals and the sharing of our experiences is why we are here. I am sure you will get the experience you seek and this is a good place to seek it.
Go to Top of Page
  Previous Topic Topic Next Topic  
 New Topic  New Poll New Poll
 Reply to Topic
 Printer Friendly
Jump To:
               

Who's On:
4 People
207.46.1..?
 Electrical Forum
65.55.25..?
 Electrical Forum
212.190...?
 Electrical Forum
95.211.8..?
 Electrical Forum
Electrical Knowledge Repository © 2000-2002 Electricalknowledge.com Go To Top Of Page
This page was generated in 0.16 seconds. Snitz Forums 2000