nm4l I recently had a NEC question that I'm not sure of - What is the total demand load in amperage on three farm buildings with 18KW, 14KW, and 12KW for single phase 120/240 volts? can anyone help? Ron.
lctrc789 nm41, I don;t know exactly what you have, or the voltage on these.
But you have a total of 56 kw at 120 volts you have 46.6 amps and at 240 you have a total of 23.3 amps.
really need to know more info but this is you total in amperage at these figures.
nm4l
quote:
Originally posted by lctrc789

nm41, I don;t know exactly what you have, or the voltage on these.
But you have a total of 56 kw at 120 volts you have 46.6 amps and at 240 you have a total of 23.3 amps.
really need to know more info but this is you total in amperage at these figures.


Thanks Pat, I don't remember the exact words, but the voltage is the same as for a single phase dwelling, only the demand is for farm. Although I have learned to solved demands in standard and optional methods for dwellings, never had to for farms yet. Ron
wareagle Are these actual measured loads or caculated loads? 220.40 is the section you need.