Subject - 20 HP motor
|
|
David Hyatt
|
20 HP motor 208 volt 3 phase, facory says install 50 amp breaker and #8 wire. This does not meet code. It must work because they do it all the time. What should I do?
|
|
David Hyatt
| Could it be that this particular motor pulls less the the code values in TBL 430.150? They said it would void warranty if more than 50 amp is installed.
|
|
David Hyatt
| Is TBL 430.150 LAW?
|
|
lctrc789
| David I know what you are saying here by the table in that article that motor has a rating of 59.4 amps. But have you seen the plate rating on this motor? I was always under the impression you go by the name plate rating if not then you go by article 430-150. The plate rating is based on the motor not the code and it could be that this motor is rated at less then article 430-150.
|
|
Ryan_J
| Hi David. You have an interesting situation here. I have always thought the table values to be a "minimum standard", but if you really think about it, the table values are used to determine the maximum overcurrent device size after multiplying the value by a percentage, based on OCPD type. With that in mind, I guess its really not a big deal. Regarding the circuit size, I would pull a # 6, like you said.
David: Could you E-mail the name of the manufacturer and the model number, if you have a minute?
Thanks
|
|
David Hyatt
| My friend called with this info last night, I haven't seen the motor as of yet, will let you know later.
|
|
David Hyatt
| It's a HAAS VF3 CNC mill machine.
|
|
wareagle
| The circuit should be 1.25 x the FLA of the motor. The code does not prevent you from installing a smaller OC device. The table lists the maximum OC device as Ryan says.
|
|
David Hyatt
| Yea, I realize that it just assuming the TBL values are correct I couldn't see a 59.4FLC motor running on a 50 amp breaker. They explained something about it is why it pulls less amperage, but I didn't get a nameplate value as of yet.
|
|
Ryan_J
| Correct...the table values are the maximum OCPD, but they are also the MINIMUM conductor size. :(
|
|
lctrc789
| Again what does the nameplate value state, this is what you need to go by.
|
|
Ryan_J
| quote: Originally posted by lctrc789
Again what does the nameplate value state, this is what you need to go by.
Nameplates are used only for seperate overload protection. See 430.6
|
|
nino
| Ryan is correct nameplates are used to overload protection.When a motor operates on a short time duty cycle,the motor windings and circuit conductor have time to cool. These motors do not require wire with a current carrying capacity of 125% of the motor full load current.The wire are sized from the percentage of nameplate current rating listed in table 430-22(a); Exception according to the classification of motor. I think 59.4 flc in table (430-150) x 85%in table (430-22(a) = 50.49 amp.(#8 wire in a 50 amp breaker) I think it.Nino.
|