Subject - 20 HP motor
David Hyatt 20 HP motor 208 volt 3 phase, facory says install 50 amp breaker and #8 wire. This does not meet code. It must work because they do it all the time. What should I do?
David Hyatt Could it be that this particular motor pulls less the the code values in TBL 430.150? They said it would void warranty if more than 50 amp is installed.
David Hyatt Is TBL 430.150 LAW?
lctrc789 David I know what you are saying here by the table in that article that motor has a rating of 59.4 amps. But have you seen the plate rating on this motor? I was always under the impression you go by the name plate rating if not then you go by article 430-150.
The plate rating is based on the motor not the code and it could be that this motor is rated at less then article 430-150.
Ryan_J Hi David. You have an interesting situation here. I have always thought the table values to be a "minimum standard", but if you really think about it, the table values are used to determine the maximum overcurrent device size after multiplying the value by a percentage, based on OCPD type. With that in mind, I guess its really not a big deal. Regarding the circuit size, I would pull a # 6, like you said.

David: Could you E-mail the name of the manufacturer and the model number, if you have a minute?

Thanks
David Hyatt My friend called with this info last night, I haven't seen the motor as of yet, will let you know later.
David Hyatt It's a HAAS VF3 CNC mill machine.
wareagle The circuit should be 1.25 x the FLA of the motor. The code does not prevent you from installing a smaller OC device. The table lists the maximum OC device as Ryan says.
David Hyatt Yea, I realize that it just assuming the TBL values are correct I couldn't see a 59.4FLC motor running on a 50 amp breaker. They explained something about it is why it pulls less amperage, but I didn't get a nameplate value as of yet.
Ryan_J Correct...the table values are the maximum OCPD, but they are also the MINIMUM conductor size. :(
lctrc789 Again what does the nameplate value state, this is what you need to go by.
Ryan_J
quote:
Originally posted by lctrc789

Again what does the nameplate value state, this is what you need to go by.


Nameplates are used only for seperate overload protection. See 430.6
nino Ryan is correct nameplates are used to overload protection.When a motor operates on a short time duty cycle,the motor windings and circuit conductor have time to cool. These motors do not require wire with a current carrying capacity of 125% of the motor full load current.The wire are sized from the percentage of nameplate current rating listed in table 430-22(a); Exception according to the classification of motor. I think 59.4 flc in table (430-150) x 85%in table (430-22(a) = 50.49 amp.(#8 wire in a 50 amp breaker) I think it.Nino.