Subject - bus drop cable
|
|
zol_man
|
quick question? at what intervals must bus drop be supported going through a commercial ceiling? thanks
|
|
lctrc789
| If you have a code book you can find all you need on bus ways in article 364-4. However busways must be supported every 5 feet unless it is marked differently. I don't know what size or type you have but being above a ceilng I would support it at least as per Manufactures recommendation.
|
|
zol_man
| found it , had internet access easier than code book. bus drop cable supported within 6 feet of bus plug then every 8 feet horizontally
|