asme3470 Hello,

Can you tell me if the code allows high voltage wiring (277) and low voltage wiring (110) in the same conduit? If so, what article in the code book says this is allowed. Thank you
JimmyDee Yes it does.

quote:
300.2(C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of circuits rated 600 volts, nominal, or less, ac circuits, and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.


Jim