Subject - Splicing??
|
|
dregsclamber
|
Can I splice the grounding conductor running from the meter base to my main grounding electrode, #6 cu , if I use a proper split bolt
What about the one going from my main to the water-pipe
I was asked to look it up but I didn't find anything that said couldn't.
|
|
Ryan_J
| You may tap to it using a split bolt, but you can't splice it unless it is irreversible.
|
|
JimmyDee
| quote: 250.64 (C) Continuous. The grounding electrode conductor shall be installed in one continuous length without a splice or joint, unless spliced only by irreversible compression-type connectors listed for the purpose or by the exothermic welding process. Exception: Sections of busbars shall be permitted to be connected together to form a grounding electrode conductor.
Jim
|
|
dregsclamber
| I thank both of you. The info was very helpful
|