Subject - Panel load balancing
|
|
David Hyatt
|
When balancing a panel with motor loads do you take the name plate amperage or the amperage in Tbl 430.150 x volts = VA per phase? Or do you take the breaker size? Example: 208 volt 3 phase 5 hp motor(name plate is 16.1amps) Tbl 430.150= 16.7amps 16.7 x 208 x 1.732= 6,016va per phase?
|
|
RS377
| Isn't a three phase motor about as balanced as you can get since its drawing the same amperage from each of the phases?
|
|
David Hyatt
| I AM SORRY SHOULD HAVE CLARIFIED QUESTION, NOT EVERY LOAD IS THREE PHASE.
|
|
Ryan_J
| I would use the nameplate, which is more accurate than the tables.
|
|
David Hyatt
| Thanks Ryan is my formula correct?
|
|
Ryan_J
| Yep, looks good to me :)
|