Subject - Service Calculation 2
David Hyatt This is a contiuation of previous post. Commercial Building.
Line Voltage 120/208 (3)phase
What size service would you install? Why?
These are the motor loads:
Pressure washer- name plate= 200 volts, 61 amps, 3phase, 20HP.
Demucking pump- name plate= 200 volts, 22 amps, 3phase, 7.5HP.
Reclaim system- name plate= 230volts, 19.2 amps, single phase, 1.5HP
Compressor- name plate= 200volts, 32.2 amps, 3phase, 10HP
The non motor loads are:
1 general purpose outlet.
(2) 2 lamp florescent lights.
(4) 250watt low bay fixtures.
(1) 20 circuit for sump pump.
(1) 15 amp cicuit gas heat.
Ryan_J What is the sqaure footage of the building, and what type of building is it?
David Hyatt It is a wash shed 50x30, with a small equipment room 20x20.
Total 1,900sq. foot.
Ryan_J I won't be able to answer you for a bit because I am leaving the office in 5 minutes, but your equipment is throwing me off a bit. Why is rated 200V? I think the NEMA standards are 208 or 230
David Hyatt The motors nameplate says 200/400 volts, I am doing my calculation at 208 volts, that is what we are running to them.
David Hyatt Ryan, this is what I come up with:
I will use actual lighting load since I know what that is.
(4) 250 low bays 4 x 250w x 125% = 1,250va
(2) florescent 2 x 64w x 125%= 160va
gas heater 15amps =1800va
largest motor 59.4amps x 208 x 1.732= 21,399va x 25%= 5,349va
motors 59.4 x 208 x 1.732= 21,399va
30.8 x 208 x 1.732= 11,096va
24.2 x 208 x 1.732= 8,718va
single phase 18.7 x 230 x = 4,301va
total= 54,073va/208 x 1.732 =150.00amp connected load
I am installing 200amp 3phase 120/208 volt service.
Will this be adequate?
Ryan_J That will do :)
wareagle David
The motors listed do not appear to be a continuous load. Do you know
if they are? Not trying to reduce your service but I wanted to check.

Bob
David Hyatt The pressure washer could be used for 3 or more hours the others probably not. The architect wanted this to be a 120/240volt 3 phase 400 amp service. I really didn't want that so I did my own calculation with the owners approval.
David Hyatt Ryan, did you See what the architect called for? Sounds like he gets paid on a percentage of what I charge.
Ryan_J Yeah, it wouldn't surprise me. I did a plan review for an electrical engineer one time, and he had a 600 amp service for a new church. One of my review items was that he needed to adjust the ampacity of one of the feeder circuits because the nuetral was non-linear, and I wanted ampacity adjustment as per 310.15(B)(2)(a). His answer...come back with a 1000 amp service!!!!

He probably didn't have to do anything at all, but I think just having a gross amount of capacity just makes some people sleep better at night, ya know? :D
veganfan Do you know what % of future use architect was planning? Could he have been plannig for larger future use.
JimmyDee
quote:
Ryan, did you See what the architect called for? Sounds like he gets paid on a percentage of what I charge.

Yep, usually 10%. That sure answers a lot of questions as to why an architect does what they do.
I installed a 400 amp service in a church years ago. Load check on a Sunday morning was less than 50 amps each leg. Over kill to say the least.
Jim