Subject - temporary wiring?
|
|
veganfan
|
AT my work place we will run wiring to j box in celling, and then us an so cord to drop out of jbox down to equipment. We do this almost every where do to the fact most equipment moves a lot. Know from what I read this would be tempory wiring unless we use cord and plug connectition on both ends. Am I reading this correctly?
400.7 Uses Permitted. (A) Uses. Flexible cords and cables shall be used only for the following: (1) Pendants (2) Wiring of luminaires (fixtures) (3) Connection of portable lamps, portable and mobile signs, or appliances (4) Elevator cables (5) Wiring of cranes and hoists (6) Connection of utilization equipment to facilitate frequent interchange (7) Prevention of the transmission of noise or vibration (8) Appliances where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance and repair, and the appliance is intended or identified for flexible cord connection (9) Data processing cables as permitted by 645.5 (10) Connection of moving parts (11) Temporary wiring as permitted in 527.4(B) and 527.4(C)
(B) Attachment Plugs. Where used as permitted in 400.7(A)(3), (A)(6), and (A)(8), each flexible cord shall be equipped with an attachment plug and shall be energized from a receptacle outlet. Exception: As permitted in 368.8.
Does this mean we would have to have a receptical in j box? Becouse we never do it is hard wired at jbox with plub at end.
|
|
iwire
| Yes, you also have to consider if you are allowed to use temporary wiring for this.
Is is it a construction site?
Is it a holiday display?
Is it a an emergency?
Is it a Test?
If not, you are may not use temporary wiring.
quote: 527.2 All Wiring Installations.
(A) Other Articles. Except as specifically modified in this article, all other requirements of this Code for permanent wiring shall apply to temporary wiring installations.
quote: 527.3 Time Constraints.
(A) During the Period of Construction. Temporary electrical power and lighting installations shall be permitted during the period of construction, remodeling, maintenance, repair, or demolition of buildings, structures, equipment, or similar activities.
(B) 90 Days. Temporary electrical power and lighting installations shall be permitted for a period not to exceed 90 days for holiday decorative lighting and similar purposes.
(C) Emergencies and Tests. Temporary electrical power and lighting installations shall be permitted during emergencies and for tests, experiments, and developmental work.
(D) Removal. Temporary wiring shall be removed immediately upon completion of construction or purpose for which the wiring was installed.
Bob
|
|
veganfan
| This is not suppose to be temp wiring it was intended to be for freaquent removal, but I feel they are screwing up. Temp wiring only good 90 days some of this been there five years.
|
|