Subject - Plastic box - metal raised roughing cover
|
|
Pierre Belarge
|
When installing a metal raised roughing cover to a plastic 1900 box, is it required to bond the raised roughing cover if the device(s) has a bonding conductor connected to it? 
If so, why, and how would you do it.
Pierre
|
|
iwire
| Pierre IMO the metal ring must be bonded.
Is there a way to do this in a code compliant manner?
IMO yes I could drill a hole in the ring and either tap the hole for a machine screw or use a nut and bolt to attach a bonding conductor.
If drilling a hole for grounding purposes is a violation I would be interested to see how others ground the enclosures of large transformers. Few come with a grounding terminal.
|
|
iwire
| Oh I forgot......Why in the world would anyone want to do this?
Get a metal box or a plastic ring Home Depot has both.
Bob
|
|
Ryan_J
| In my opinion, the device's 6-32 screws bond the plaster ring and nothing else is required. We allow a metal plaster ring to ground a switch if there is metal to metal contact, why wouldn't the opposite hold true?
I think 250.4(A)(5) would require it.
|
|
iwire
| quote: Originally posted by Ryan_J
In my opinion, the device's 6-32 screws bond the plaster ring and nothing else is required.
IMO that conflicts with 250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes.
Once the device is removed you have lost grounding continuity.
I guess this one is over my head we don't use plastic boxes or rings.
|
|
Ryan_J
| Thats a good point Bob. I've never put much thought into this either, kind of an oddball, isn't it?
|
|
Pierre Belarge
| I believe the ring needs to be bonded regardless of the device connection. The way we do it here is with a grounding clip, with either a tail to the device or selfgrounding devices.
|