If you have a 3 phase 225 amp main breaker, what is the max you should read with a amp clamp per phase? 225/1.732? What about single phase 200 amp?
|
|
Ryan_J
| I would say 80% of 225
|
|
cs409
| a 3 pole 225 amp 3phase main breaker is protection for 225amps per phase...as a 2 pole 200amp single phase is 200amps per pole etc etc........either leg of that CB exceding its limit, will trip all phases/poles,,,,or suppose to! hope this helps.....
|
|
JimmyDee
| Because most breakers have both a thermo unit and magnetic short circuit trip, you may see higher amps for short periods of time than the rated size. Jim
|
|
David Hyatt
| If thats the case then, then you could actually pull four hundred amps balanced perfectly at all times, on a 200 amp main breaker. 200 amps on phase 1 and 200 amps on phase two???? Then you would be over the panel rating? But in theory this is true??????Right??// Don't seem right but does make sense. 3/0 copper is 200amps per phase. More comments please.
|
|
JimmyDee
| Yes, you are correct but you would not have overloaded the panel because it is rated for 200 amp at each leg. Jim
|
|
cs409
| that is why you see a lot of over kill with the DIY installs,,,they dont understand its per pole/phase...
|
|
renosteinke
| One detail: with three-phase systems, it is possible that there is "harmonic distortion" that will throw off your meter reading. By comparing the reading from a "true RMS" and a "standard" amp-clamp, you can see just how much harmonic distortion is present. As a rule of thumb, if there is 12%-15% (or more) difference between the readings, you will want to look into dealing with the problem.
|