What size Quadraplex is needed for a 120/208 3Ph 600A commercial service?
|
|
Ryan_J
| You'll probably want to go with parallel. I can't answer your question because I need to know the computed load. 230.42.
|
|
JimmyDee
| Looks like paralled aluminum 250 kcmil would be big enough but I know like Ryan_J stated it would depend on computed load. Power company would probably run a #2 or #1 and call it good. Jim
|
|
iwire
| Is this a NEC installation or a NESC installation (Utility Code)?
The utility's have good reasons for the size wires they choose.
Generally 50% of what the NEC would require, this is not simple because they are being cheap.
By the way I hope you have the right equipment to pull the sag out of 250 AL quadraplex.
|