Subject - 2 ton window airconditioner
|
|
jakeselectric
|
I am installing a 2 ton window airconditioner. Is the following information correct.
240 volt dedicated circuit, #12 awg THHN wire on a 20 amp 2 pole breaker
|
|
JimmyDee
| Just off the top of my head, I'd say it is not big enough but do you have the amp rating for the AC unit? Jim
|
|
jakeselectric
| quote: Originally posted by JimmyDee
Just off the top of my head, I'd say it is not big enough but do you have the amp rating for the AC unit? Jim
No I don't have the amp rating, it is an old unit that the customer has and I can't find the rating anywhere. I don't think it will pull more than 20 amps but I guess I could run # 10 on a 30 amp but I don't want to over rate the airconditioner either.
|
|
kbsparky
| What is the NEMA configuration on the attachment plug? If it has a NEMA 6-20P on it, then you install a 20 Amp circuit. IF there is a NEMA 6-30P, then install a 30 Amp circuit. No brainer 
|
|
jakeselectric
| well I would say you are right and I should have figured that out on my own. Thanks to both of you for the help.
|
|
kbsparky
| Jake:
Sometimes, the obvious stares us in the face, and we can't see the forest for all those trees in the way 
FWIW, I used to install circuits for window A/C units, and about the largest size that operated on a 20 Amp circuit was 25,000 BTU. Just a hair above 2 "ton"
|
|
lctrc789
| 24,000 I think is 2 ton and 30,000 is 2 1/2 ton and so on at least from what I remember.....
|