Subject - 200 amp residential transfer sw
stedder Can I use the numbers in table 310.15(B)(6) for sizing feeders from a generator set to the auto transfer switch, or is the table for main service feeders only?
kbsparky I would think those wire sizes are appropriate, as long as you are dealing with a dwelling unit. Gotta be an expensive setup, if you are installing a generator set capable of delivering the full load required such that the rating is the same as the supplying utility
stedder Thanks Ken, Customer supplied switch and generator, set in place, installed 200 gal lpg tank and saved the wiring for me. Oh did I mention he buried 2" pipe w/ 4 45 degree bends (hope they're not 90's) that's why I want to keep the wire size as small as possible and I wasn't sure if I'd seen need for full or oversized conductors somewhere. Now that I think about it, the generators' rated output was 166.6 amps and I think he said that and the switch was $10000.00 but...it is part of keeping his wife happy through a divorce settlement.
wareagle If you are going to bury the conductor in conduit it will have to be designated as suitable
for wet locations.