jimmy
Avid Member

USA
105 Posts

Posted - 03/09/2010 :  09:07:23  Show Profile  Visit jimmy's Homepage  Reply with Quote
I am bidding a service feed to a new x-ray machine.According to the nec the disconnect means shall be operable from a location readily accessible from the x-ray control.(517.72 (B)). The room layout shows the x-ray control outside the room proper. My question is do I locate the disconnect in a general use area(hallway) or is the control circuit going to satisfy the emergency shut down of the equipment?

rabbitgun
Forum Magnate

USA
2035 Posts

Posted - 03/09/2010 :  16:42:39  Show Profile  Visit rabbitgun's Homepage  Reply with Quote
Isn't the controller where the operator stands?

An analog man in a digital world.


Go to Top of Page

Top Hand
Member

Canada
49 Posts

Posted - 03/09/2010 :  18:25:49  Show Profile  Visit Top Hand's Homepage  Reply with Quote
Is the purpose for this rule to protect the operator or to protect the technician repairing the device? the answer to this question would change the location of the disconnect.

The Day you stop learning is the day you die
Go to Top of Page

jimmy
Avid Member

USA
105 Posts

Posted - 03/15/2010 :  05:59:33  Show Profile  Visit jimmy's Homepage  Reply with Quote
The x-ray operation control is a low voltage switch that controls the equipment contactor so in effect the operator "controls" it from a remote location.My question is if the disconnects purpose in this rule for emergency shutdown or repair safety. If for emergency it should be at the operator position. If for equipment repair at the equipment. The disconnect by the way is 100 a non fused lockable.
Go to Top of Page
  Previous Topic Topic Next Topic  
 New Topic  New Poll New Poll
 Reply to Topic
 Printer Friendly
Jump To:
               

Who's On:
3 People
Google Bot
 Electrical Forum
204.2.16..?
 Electrical Forum
84.140.2..?
 Electrical Forum
Electrical Knowledge Repository © 2000-2002 Electricalknowledge.com Go To Top Of Page
This page was generated in 0.14 seconds. Snitz Forums 2000