Posted - 02/06/2010 :  10:58:39  Show Profile  Visit millspgh's Homepage  Reply with Quote
I am giving a customer some different options on a project where his shopping center sign was never wired. I found the feeder conduit to be broken under the parking lot. It is a long way from the electric room to the sign, maybe 400-500'. There is a light pole 25' away from the sign, the lights are single phase 208 volts. Do they make a transformer I can put between the 2 to go from 208 down to 120 without having a neutral on the primary? Can the transformer produce a neutral from a ground?

Thanks in advance for your thoughts.

Paul Miller
Heritage Electrical Services

rabbitgun
Forum Magnate

USA
2035 Posts

Posted - 02/06/2010 :  11:32:57  Show Profile  Visit rabbitgun's Homepage  Reply with Quote
A darn good question and have a very similar situation right now.

Here is what we found:

277v lighting feeding the lot poles. They then fed a single phase transformer to go from 277 to 120 for the sign. They bonded one side of the secondary to the grounding conductor to create the neutral but I did not like it so I have recommended that the ballasts for the sign be changed out to 277v and eliminate the transformer.

An analog man in a digital world.


Go to Top of Page

rewire
Member

45 Posts

Posted - 02/06/2010 :  12:06:34  Show Profile  Visit rewire's Homepage  Reply with Quote
quote:
Originally posted by rabbitgun

A darn good question and have a very similar situation right now.

Here is what we found:

277v lighting feeding the lot poles. They then fed a single phase transformer to go from 277 to 120 for the sign. They bonded one side of the secondary to the grounding conductor to create the neutral but I did not like it so I have recommended that the ballasts for the sign be changed out to 277v and eliminate the transformer.

they have correctly installed the transformer.XO must be bonded on a seperatly derived system the bond does not create the neutral.
Go to Top of Page

rabbitgun
Forum Magnate

USA
2035 Posts

Posted - 02/06/2010 :  12:16:39  Show Profile  Visit rabbitgun's Homepage  Reply with Quote
quote:
Originally posted by rewire

XO must be bonded on a seperatly derived system the bond does not create the neutral.



Agree but bonded to what kind of ground? Just the grounding conductor available?

An analog man in a digital world.


Go to Top of Page

rewire
Member

45 Posts

Posted - 02/06/2010 :  13:32:49  Show Profile  Visit rewire's Homepage  Reply with Quote
quote:
Originally posted by rabbitgun

quote:
Originally posted by rewire

XO must be bonded on a seperatly derived system the bond does not create the neutral.



Agree but bonded to what kind of ground? Just the grounding conductor available?

you can also drive a ground rod at the transformer and bond the neutral XO to the new ground system.
Go to Top of Page

RS377
Forum Magnate

USA
1009 Posts

Posted - 02/06/2010 :  19:39:37  Show Profile  Visit RS377's Homepage  Reply with Quote
We are required to run a ufer ground at all pole lights, so that would be available.

Taught well
----Full time contractor May 18th, 2007
Go to Top of Page

rabbitgun
Forum Magnate

USA
2035 Posts

Posted - 02/06/2010 :  21:19:10  Show Profile  Visit rabbitgun's Homepage  Reply with Quote
quote:
Originally posted by RS377

We are required to run a ufer ground at all pole lights, so that would be available.



By whom?

An analog man in a digital world.


Go to Top of Page

RS377
Forum Magnate

USA
1009 Posts

Posted - 02/06/2010 :  22:46:19  Show Profile  Visit RS377's Homepage  Reply with Quote
San Jose, Ca.

Taught well
----Full time contractor May 18th, 2007
Go to Top of Page

bytemylobster
Avid Member

Canada
409 Posts

Posted - 03/31/2010 :  10:36:53  Show Profile  Visit bytemylobster's Homepage  Reply with Quote
I would just change the lamp ballasts to multi-tapped to match the voltage at the lamp location.
If the feed was broken under the lot, I would use a tracer to locate the break and repair it.
Go to Top of Page
  Previous Topic Topic Next Topic  
 New Topic  New Poll New Poll
 Reply to Topic
 Printer Friendly
Jump To:
               

Who's On:
3 People
207.46.1..?
 Electrical Forum
207.46.2..?
 Electrical Forum
Google Bot
 Electrical Forum
Electrical Knowledge Repository © 2000-2002 Electricalknowledge.com Go To Top Of Page
This page was generated in 0.15 seconds. Snitz Forums 2000