avisas
|
I am wiring new 110V outlets in my basement. The circuit breaker is 20A. I need to connect about 10 outlets on that circuit using 12-2 wire. Is that the correct type?
Thank you
Avi
|
|
JimmyDee
| For regular, 120 volt outlets protected by a 20 amp breaker, yes you would use 2 conductor #12 with ground romex. Jim
|
|
avisas
| Thanks Jim!
Should I be concerned if some of the exisiting outlets use 14-2 wires? Do I need to replace the wires with 12-2 type?
Avi
|
|
JimmyDee
| quote: Originally posted by avisas
Thanks Jim!
Should I be concerned if some of the existing outlets use 14-2 wires? Do I need to replace the wires with 12-2 type?
Avi
14-2 wire needs to be protected with a 15 amp breaker. If you are using an existing circuit and it has 14-2 wire in the circuit, feed it with a 15 amp breaker or make sure all the wire in that circuit is 12-2. We normally don't try to give help here to do-it-yourselfers because of the possibility of misinterpretation of information. I would recommend you obtain professional help for your project. Jim
|
|
avisas
| Thanks! I will follow your advice. Avi
|