Subject - SERVICE CALCULATIONS
|
|
David Hyatt
|
The books I have on commercial feeder calculations, that helped me pass the master test, don't seem to help much in the real world. Step 1)TBL 220.3(A) lighting load ___VA x square foot. Step 2)TBL 220.11 Demand Step 3)220.21 Compare heat and air omit smaller. Step 4)220.3 loads of outlets Step 5)220.13 demand Step 6)220.20 Demand kitchen equipment. Step 7)220.14 Largest motor increased by 25% Step 8)Size service by dividing total VA by line voltage. My big problem is what if you have 5 large motors that could run continuous, this formula does not take that into consideration. I will make another post for the actual loads. Question: If all loads are know do you use the formula above or calculate actual loads?
|
|
Ryan_J
| Are these motors that you speak of hermeticly sealed (A/C units)?
|
|
David Hyatt
| No. Pumps and compressors.
|
|
Ryan_J
| 220.3(B)(3) refers you to 430.24. 430.24 requires 125% of the largest motor plus 100% of the other motors.
Does that answer your question?
|
|
David Hyatt
| Yes, and am I right to say if all loads are known use those figures instead of the lighting and receptacle loads in my formula?
|
|
Ryan_J
| No. You have to design to article 220.
I know this sounds stupid, and in my opinion, it is. For example, (off the top of my head) an office requires 3(?)VA per sqaure foot, right? Well, the energy code only allows you to connect like 1.5VA per sqaure foot...but you still have to design for it.
Let me see if I can find a proposal by a freind of mine named Noel Williams for the 2005 that got shot down. I'll post it as soon as I can find it.
|
|
David Hyatt
| What if this doesn't fall under a category listed in the table for lighting loads? I was thinking I could do it by connected load?
|
|
Ryan_J
| Here is the proposal, and the panel's response:
quote: Submitter: Noel Williams Herriman, UT Recommendation: Add a new Exception to read as follows: "Exception: Where other codes or standards limiting the amount of energy that may be used for lighting in a specified occupancy are adopted by the authority having jurisdiction, the unit loads for those occupancies shall not be required to be larger than the maximum unit load permitted for that occupancy." Substantiation: The existing unit loads for certain occupancies, especially office buildings and banks, are significantly higher (almost double) the unit loads permitted by model energy codes for those same occupancies. For example, energy codes may limit lighting loads in office buildings to about 1.8 VA per square foot, which is entirely adequate where electronic ballasts and T-8 fluorescent lamps are used. (In fact, one intended effect of the energy codes is to require such energy efficient sources.) Nevertheless, these real loads are not permitted to be used under the current language of this section. The existing unit loads do not consider (or encourage or reward) the use of modern energy-efficient lighting sources. Furthermore, once this artificially high calculated load is determined under 220.3(A), it must be treated as a continuous load for purposes of determining minimum feeder or service capacity. Currently, Example D3 in Annex D shows a case in which the real load is slightly less than the calculated load, and the calculated load is taken at 125 percent for sizing feeders or services. The difference is not significant in this example, but the requirement illustrated by the example is very significant when the maximum load permitted by a jurisdiction is only about half of the phantom "calculated" load derived from this section. This is a very severe penalty for occupancies with large floor areas. Since the permission to reduce unit loads is conditional on the adoption of a limit on the use of energy, this proposal will not compromise safety. Currently, the only way a jurisdiction can recognize lower calculations under the NEC is by special permission, which means special permission must be issued on every such project. The primary argument in favor of retaining the higher numbers is that it tends to build in a significant amount of spare capacity which may be used later under the provisions of 220-35. However, spare capacity is not an intended outcome of complying with the NEC 90.1(B). Panel Meeting Action: Reject Panel Statement: See the panel action and statement on Proposal 2-299 (Log #2880). Number Eligible to Vote: 13 Affirmative: 13
And the panel's response:quote: Panel Statement: The current requirements of this section are not in conflict with energy codes. The requirements of Article 220 provide means to calculate adequate service and feeder load capacities but does not require that this entire capacity be connected. Number Eligible to Vote: 13 Affirmative: 11 Negative: 2 Ballot Results: Explanation of Negative: BECKER: I concur with Mr. Dobson's Explanation of Negative Vote. DOBSON: The proposal seeks to allow the electrical designer the option to use different lighting power densities based on other mandatory codes in a given jurisdiction. In specific localities with mandatory maximum lighting power densities based on energy code requirements, power density maximums are less, often by half, than those of the NEC. Yet the designer is not permitted to take advantage of the potentially lower cost electrical system where higher efficiency fixtures are not only allowed, but required. An example is the state of Massachusetts commercial energy code that specifies the interior and exterior lighting power allowance permitted for different types of facilities; offices for example have a maximum of 1.3 watts per square foot whereas the Table 220.3(A) specifies 3.5 watts per square foot.
I liked Noel's finishing statement, where he states that what is happening conflicts with 90.1, purpose and intent of the code.
|
|