Subject - GFCI's Question.
twildenhaus In 2002 nec there is suppose to be gfci,s in bedroom,s now. can I put one gfci oulet at the beginning of my run and have this to code. because the first one protects the run right.
justinelect I believe your are asking about AFCI's. As per 210.12(B) 2002 NEC
quote:
All branch circuits that supply 125-volt, single phoase, 15- and 20-ampere outlets installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter listed to provide protection of the entire branch circuit.

Right now I believe the only AFCI devices available are breakers. Another thing I would point out is these AFCI devices do not work on multiwire branch circuits.

Justin
JimmyDee
quote:
Originally posted by twildenhaus

In 2002 nec there is suppose to be gfci,s in bedroom,s now. can I put one gfci oulet at the beginning of my run and have this to code. because the first one protects the run right.


This is not correct. Again I would recommend, a professional licensed electrician.
Jim
twildenhaus Thank You for the info. The reason of confusion is because the approved plans by the county say gfci is required in bedrooms which is a mess-up on there part and I will let them know. I checked the nec and know what is required.thanks guys.
Pierre Belarge

UL has 6 different listings for AFCI devices:
1. Branch/Feeder Type (AVZO)
2. Combination Type (AWAH)
3. Cord Type (AWAY)
4. Outlet Branch Circuit Type (AWBZ)
5. Outlet Circuit Type (AWCG)
6. Portable Type (AWDO)

Of the six, No.1 is the most common and is the one most of the electricians are using - it is the breaker type.
No. 2 is the combination type which should be on the market soon if it is not already. This type offers the best protection - circuit conductor protection as well as cord protection of appliances, etc... that are plugged into the receptacle - which No 1 does not protect.

The other types are not available yet.

Not all jurisdictions are requiring AFCI protection, and you should contact the AHJ to find out what the requirements are in your area of work.

Pierre