Subject - wiring for hazardous loc
ageman I have a situation where i have one existing fuel tank with a pump. Two more tanks have been set at the same location with the same amperage motors as the existing pump.
I want to use the same circuit for the other two pumps. I beleive that as long as i seal both sides within 18" of a enclosure, i can continue this circuit for the two new pumps.

I do not need a seperate circuit for each pump, correct.

thanks
Ryan_J Correct. :)
cs409 u will need to meet ART. 514.11(A) along with 514.11(B)(for attended) or 514.11(C)(for unattended)....for disconnect means... reguardless if this is a motor fuel dispensing place or bulk storage(Art 515.10 which reverts u back to 514.11 for disconnects).