Subject - Bath Tub Jacuzzi Hook up
Ingram321 Do i install a GFI 20amp receptacle? or is direct wired? If direct wired than I assume GFI breaker for protection right?
Scott Vickrey Hydromassage bathtubs and associated components must be protected by a GFCI. All receptacles in a bathroom need to be GFCI protected. All the metal piping if any, electrical equipment metal parts and pump motor must be bonded together with a #8 solid copper wire. Unless the motor or equipment is labeled to be double insulated. If something is double insulated then it must not be bonded.
If the motor came with a plug on the end of the cord then, yes have a GFCI receptacle installed. If you need to direct wire it use a GFCI breaker.
David Hyatt Scott, you mentioned double insulated motors before. Will you explain why not to bond them.
Scott Vickrey You don't bond double insulated equipment because doing so will defeat the double insulation protection. See section 680.26(B)(4).
Ryan_J Scott: I think the appropriate section would be 680.74, but it does say the same thing.
David Hyatt I see the code ref. but don't understand the thoery behind it. I guess double insulated has no chance of becoming inergized? What would it hurt to bond it ?