Subject - Romex
|
|
David Hyatt
|
If you have a piece of romex pulled tight between 2 locations, instead of setting two j-boxes to add another recept. is there a better or easier way. This is for existing wiring. I seen a few years ago a tee shaped connector that pressed on romex, do they still have those, and are they safe?
|
|
JimmyDee
| I they are accessible, I cut the one short or take the romex out of one box and run it to where it is needed, splice it in the new box and run a new piece to the box where you removed the romex from. If you can't get at it, I think you have the best solution in your question. Jim
|
|
Scott Vickrey
| David I have never seen anything like you described.
|
|
David Hyatt
| I finally found the splice connection I was looking for, check this out. http://www.molex.com/product/sterm/coc3.html
|
|
Scott Vickrey
| I wonder how much those puppies cost?
|
|
cal_sparky
| I looked into these once--keep in mind that like any splice, they must remain accessible w/o disturbing the finished surface of the building. They would work for an accessible attic or similar, but CANNOT be buried in a wall or inaccessible ceiling.
And since they are designed and sold as a tap, they cannot properly be used as a simple splice.
Given these limitations, they don't offer much advantage over the conventional approach.
Cliff
|
|
David Hyatt
| I am not sure Cliff what you mean by a simple splice? I was going to use them in crawl spaces. They are UL listed as a self contained j-box.
|
|
Electricman
| Since they are UL listed as a j-box there should not be a problem with these. If you look into it farther it looks as though they use them to join conductors on mod homes. I would say the only problem with them would be with the AHJ and how he would interpret code.
|