David Hyatt 1) What size disconnecting means is required for a 3hp, 230volt, single phase motor?
A)20amp B)25amp C)30amp D)40amp

2)What is the min. size EMT conduit permitted which contains the following conductors?
5- #14RHH with outer covering
6- #10THW
5- #12RHW without outer covering
2- #6XHHW
1- #8 Bare copper
a)1" B)1 1/4 C)1 1/2 D)2"
JimmyDee Looks like an 1 1/2" will do it if my math is correct.
Chapter 9, table 1, looking at the EMT chart and 40% fill for conduits with 2 or more conductors we see that 40% of the total area for 1" is .346 sq in; 1 1/4" is .598 sq in; 1 1/2 is .814 sq in and 2" is 1.342 sq in.
The following areas of conductors are found in Chapter 9 tables 5 and 8.
#14 RHH is .0145 sq in X 5 = .0725 sq in
#10 THW is .0333 sq in X 6 = .1998 sq in
#12 RHW is .0260 sq in X 5 = .13 sq in
#6 XHHW is .0590 sq in X 2 = .118 sq in
#8 Bare is .017 sq in X 1 = .017 sq in
Adding, the total is .7173 sq in an that is greater than the 1 1/4" area @ 40% but less than the .814 sq in of the 1 1/2" so it would be the 1 1/2" conduit.
Now for the other one. (good thing I'm on Spring Break this week)
Jim
JimmyDee Looks like a 20 amp will do. Not sure I would use one this small but it seems like the code says it is OK.
Artical 430.110 says The disconnect is to be at least 115% of the motor's full load amps and in artical 430.148 a 3HP single phase motor's FLA is 17 amps. 115% of 17 amps is 19.55 amps. A little close, but.
Jim
David Hyatt Jimmy, Some of your values in the tables for question 1 was wrong, I think I have the right answer which is B) 1 1/4, Tom Henry says 1 1/2 also, he has the same values as I do but the answer is different. You definatley knew where to go to find the answer.14RHH with outer covering is .0293 / 10THW is .0243, change these values and see if 1 1/4 will work.
As for question 2)I came up with the same answer as you but can you buy a 20amp disconnect? I thought this was a trick question because 30 amp is the smallest you can buy?
Thanks for your help,
David
JimmyDee You are correct about the mistake of the wire size. I just remembered a glitch one of my students found on the #10 THW wire. You are correct about the area of that wire, however, in the early code books of the 2002 printing, which I have, the #10 THW is listed in 2 places with 2 different areas and I am sure that has been changed. The one I used was listed as .0333 sq inches but a little common since would have told me that was not correct. I did screw up on the #14 wire.
However, I still come up with .7368 sq in and that is 1 1/2" conduit. I hate this kind of stuff. Yes you are correct about the disconnect size being a 30 amp as the smallest. I got a mind set on a double pole, 20 amp switch, forgetting that they are not HP rated. Maybe I don't hate it too much as I actually had fun showing the world someone that has been around 40+ years in the electrical trade can still make mistakes.
Jim
David Hyatt Heres what I have in 2002 code:
#14RHH with outer covering .0293 X 5= .1465
#10THW .0243 X 6 = .1458
#12RHW without covering .0260 X 5 = .13
#6XHHW .0590 X 2 = .118
#8Bare stranded = .017
_______
.5573 sq. in.
table 4 EMT 1 1/4 =.598 would be OK right?
JimmyDee You are 100% correct.
Jim
David Hyatt Tom Henry was wrong on several answers in his new book, about 5 I think. But there are probably 500 questions so I gues thats not bad. I just get so confused when he makes mistakes, I second guess myself until it drives me crazy. I just finished my master calculations practice exam and only missed one. Hope I can do as well on the 17th when I do it for real.
Scott Vickrey Good luck on the test David.
This is actually a good question. We should do more of these. Maybe one a week. I would recommend one question per topic.
Sorry I've been out. I've been repairing storm damage.