Subject - Bathroom Circuits
|
|
Sparky2
|
In the 96/99 code book you were to use a 20 amp recept. for the bathroom that could only be used in conjuction with another bathroom. In the residential area that I am now working we are using recept and lighting for a bathroom together. Is this common practice or has the code changed????
|
|
blackrd
| In my area, it has always been ok for the bathroom circuit to provide for all loads in that bathroom, no appearances of that circuit anywhere else. receptacles, lights, fan, heater,etc. I havent heard of one circuit for 2 bathrooms. Maybe that has always been allowed, in my area.
|
|
Ryan_J
| You can feed all of the receptacle outlets in all of the bathrooms, or you can feed everything in one and only one bathroom. 210.11
|
|
Sparky2
| I have been working commercial for the past few years and I have just got back into residential. We ran 1 circuit for Bathroom - one B/R designated as the line side of a GFI - whether it it be 1, 2, 3 B/R's in house - was able to share that circuit - the logic contrator wise is that you could buy only 1 GFI and regular recept's in the other B/R's. As for the lighting it shares w/other lighting circuit except for the shower light which had to be on a faceless GFI. Now bathroom shares power and lighting except for HVL's which has it's own circuit.
|
|
Sparky2
| quote: Originally posted by Ryan_J
You can feed all of the receptacle outlets in all of the bathrooms, or you can feed everything in one and only one bathroom. 210.11
Are you saying that this is 2002 code that bathroom GFI can share w/ lighting circuit. This will also take care of shower lights?
|
|
Electricman
| Sparky2, Check out 210.11(3) and 210.23(A) when using the GFCI to supply the lighting in a bathroom. Remember that circuit can only supply 1 bathroom when its a GFCI/Lighting combo circuit, the circuit cannot supply another bathroom.
|
|
Ryan_J
| quote: Originally posted by Sparky2
quote: Originally posted by Ryan_J
You can feed all of the receptacle outlets in all of the bathrooms, or you can feed everything in one and only one bathroom. 210.11
Are you saying that this is 2002 code that bathroom GFI can share w/ lighting circuit. This will also take care of shower lights?
Yep, pretty much, as long as the circuit doesn't leave the bathroom.
|