Subject - 12 wire on a 15 amp circuit
|
|
Rob96
|
Is it ok to use 12 wire on a 15 amp circuit? Thanks.
|
|
Ryan_J
| Yes. You're welcome.
|
|
Rob96
| Thanks Ryan. I was almost sure of it, but wanted to ask. Thanks again.
|
|
kbsparky
| quote: Originally posted by Rob96
Is it ok to use 12 wire on a 15 amp circuit? Thanks.
Actually, in some cases, due to long runs and voltage drop considerations, it is preferable to use a 12 wire on a 15 Amp circuit. I know of some contractors who automatically use the next larger size wire for his home runs back to the panel, once the length exceeds 100 feet.
|
|
luckyshadow
| If you are using # 12 for the entire circuit it's great. If you are using #12 for , lets say the homerun , then dropping down to # 14 I would suggest placing a tag on the conductors at the panel. By tagging these conductors some future electrician won't place them on a 20 amp breaker, which would be too large an overcurrent device for the #14.
|
|
banditfrompa
| I thought that you could not mix wire sizes.
|
|
Ryan_J
| quote: Originally posted by banditfrompa
I thought that you could not mix wire sizes.
You can if you protect them properly.
|