johnj trying to find a answer in syracuse NY what is the largest size copper conductor needed for driven ground
lctrc789 The largest size copper conductor for a ground rod never has to be larger than # 6 wire. Article 250-50 (a)2.
johnj
quote:
Originally posted by lctrc789

The largest size copper conductor for a ground rod never has to be larger than # 6 wire. Article 250-50 (a)2.

That's what I thought thanks 2002 nec 250.66(a)
Energreen
The utility company may have a different requirement from the NEC. I don't know their reasons, but RG&E requires a #4 ground electrode conductor.
Alfred It's the same here in Tennessee.
Thanks ALFRED JOHNSON
lucky1122 NEC requires nothing larger than #6 awg cu but remember how you layout the connection may change that . For instance lets say you daisy chain the connections from one electrode to the other well then the largest size would be called for depending on what the electrode is >